It may be helpful to identify the poles. First, find each pair of leads with continuity. Next, apply DC to each pair in turn and use a battery to identify location and polarity of the poles.
One of our winding experts will give you more specific instructions.
Typo: I meant to say;
"Use a compass to identify the location and polarity of the poles."
Bill,
So what you are saying (after I mark original connections) is to break the 2 wyes, and the 3 pairs on the 3 leads, and find the ends that have continuity? This would give me 12 individual leads coming off the coils, not including the coil pairing connections which I would assume are left intact… After I’ve marked these pairs, how do I determine “lead polarity”? with the compass? THANKS AGAIN BILL !
Motorwinder,
2 wye connection. Could be 440 or 220. Normally, we'll mark the voltage on the nameplate when we rewind them to 3 leads.
I definitely have 2 sets of three leads connected centered about 180 degrees out… The other 3 pair are connected to the 3 leads A/B/C… The plate wasn’t marked that I can see…
If you want 9 leads, take it to a motor shop. They can determine if you need 1-2 wye, or 2-4 wye.
I was trying to do this myself, as I had leads put on another motor FOR $220 that may be too big… THANKS FOR YOUR TIME!
Hello Integrity
Your motor name plate is indicating the voltage is 220/440 but your connection is only for one voltage. So you most identify the right connection voltage.
in this case the best is test the motor with no load and note N.L.Current, test first with 220 Volts if N.L.current is between 12 to 20 Amperes then the motor is connected for 220 V. But if you found a N.L.Current between 3 to 4.8 the motor is connected for 440 V.
The no load idle current is what prompted me to suspect this was internally wired for 440V. Connected to SINGLE PHASE 220 (measured 245), and run up with a pony motor, my no load idle current was 6.6A/leg… Or 30% over, which would line up perfectly with 1 phase not helping…
The connection that you found is two stars, but we don´t know the right design connection, Best way is N.L. Test.
If you need both voltages or the winding is connected for the wrong voltage the motor need to go to one shop for reconnection.
Definitely connected for the wrong voltage… I would like to change it to 220, myself… AND ideally wire the nine leads to the correct combination of 12 winding taps! THANKS FOR YOUR HELP CARLOS!
I guess the basic question here for everybody is:
1. How can I identify these 12 taps coming from the coils, and how do I connect 9 leads to 12 taps??? I am of course assuming that the other 12 connections “between coils” remain intact…
I want to thank everybody again… it really is great to have people that take the time to help others for no other reason than generosity of your knowledge….
Ed