RH and DB temperature 1
jrrocks
58
I might have asking a silly question. Can we reduce the relative humidity, subsequently WB of air without changing the dry bulb temperature.
yes, while the wet bulb depression (the difference between the dry-bulb temperature(Air temperature) and the wet-bulb temperature)comes to close , the rh will increase, and vice versa
The answer is both no and partly yes. First of all, if you need to reduce relative humidity, you need to cool air and take its water content. Therefore, you decrease DB. However, when you finished to decrease water content, then you can heat air to the inital DB. Then, you have DB unchanged and Rh decreased. Please try to draw process in psychrometric chart. It had better to do it for understanding.
A desiccant system would be one way to deliver this result. the process is pretty much as Emrelug describes above
Typically in a cooling coil, we do cooling and dehumidification, which means reduction of Dry Bulb and RH. However, if in the process of dehumidification, we end up over-cooling, then a sensible heat addition is done to bring back the temperature of air to the desired level.
HVAC68
No.
You can reheat to change DB temperature after reducing WB temperature.