Rigid Conduit thread sealant-any acceptable? 1

Status
Not open for further replies.

EvanH

Mechanical
Mar 7, 2003
14
Reading NEC's sections on IMC and Rigid Conduit, I can't spot any definitive rules on whether pipe sealant is allowed or forbidden. Clearly it seems that using a compound which prevented electrical conductivity would be undesirable, but does anyone have any specific guidelines they could point me towards?

Also, are there any guidelines on this issue that would be specific for Class I Division 1 Hazardous Locations?

Thanks! -Evan
 
Replies continue below

Recommended for you

I suspect if there is any requirement one way or the other, it would be in UL. I'm just a dumb engineer, not an electrician, but I don't think any compound is used on the threads.

Check out this little guy:


Maybe it will be of some help.
 
For a listed product, suggest T&B “Kopr-Shield” Don’t expect a perfect watertight seal, but preservation of raceway continuity during faults. Page 11 of
Another unlisted similar copper-particle antiseize paste is FelPro 'C5A'
For hazardous-location installations, Crouse-Hinds HTL or STL compounds are intended for the purpose.
Silver-particle antiseize pastes are Cool-Amp 'Conducto-Lube' and SwageLok 'Silver Goop'.
Page 11 of
Nickel-bearing compounds are Bostik-Findley ‘Never-Seez’ Pure Nickel Special and ‘Never-Seez’ Nickel Special, Nuclear Grade.

 