qman5
Electrical
- Sep 10, 2012
- 28
Hello all,
In the case of ungrounded system, where the SLG fault current is sensibly 0, or in the case of a NGR, limited by the NGR current, do you typically size the grounding pigtail risers for this limited current, or the maximum fault current (e.g. LLL, LLL)? Consider an ungrounded delta system inside a substation.
Would a scenario like LL-G not bypass the NGR, but still, would we see an appreciable fault current in the riser (assuming flashover from LL to ground)? I don't see this.
Is there any scenario where the riser could see more than the ~0A or NGR-limited current? As it stands, I would presently size the riser for 500 MCM going by IEEE 80, but I really question if it's necessary to have such a cross sectional area, of if less can be argued. The cautious approach would be to go with the full 500MCM, but may be unoptimized.
In the case of ungrounded system, where the SLG fault current is sensibly 0, or in the case of a NGR, limited by the NGR current, do you typically size the grounding pigtail risers for this limited current, or the maximum fault current (e.g. LLL, LLL)? Consider an ungrounded delta system inside a substation.
Would a scenario like LL-G not bypass the NGR, but still, would we see an appreciable fault current in the riser (assuming flashover from LL to ground)? I don't see this.
Is there any scenario where the riser could see more than the ~0A or NGR-limited current? As it stands, I would presently size the riser for 500 MCM going by IEEE 80, but I really question if it's necessary to have such a cross sectional area, of if less can be argued. The cautious approach would be to go with the full 500MCM, but may be unoptimized.