FX103
Mechanical
- Feb 15, 2008
- 3
I'm doing clamps spacing calculations for a 6" risers to be installed on a jacket.
I'm using criteria of fatigue analysis due to VIV and direct wave action (DNV RP F105). Are they applicable out of the submerged zone but inside the splash zone? If not, which kind of criteria should be used? Only static?
Thanks for any help
I'm using criteria of fatigue analysis due to VIV and direct wave action (DNV RP F105). Are they applicable out of the submerged zone but inside the splash zone? If not, which kind of criteria should be used? Only static?
Thanks for any help