could someone please explain the main difference between a ring main unit and MV switchgear. in a substation do we have to have the two?
 
Replies continue below

Recommended for you

Switchgear is a fairly generic term for equipment which incorporates switches or circuit breakers.

An RMU is a specific type of switchgear comprising a pair of switches for a ring circuit to loop in and out, plus a switch-fuse or breaker for the tap-off feeding the load, all integrated into a single unit.
 
In MV switchgear, you can have incomings and outgoings as per load. But in RMU it is mainly two incomings+1 outgoing so that your outgoing power is not disturbed.

Thanks,
Vijay
 
But, RMUs with multiple feeders are also available in the market. This is a variation of the basic RMU.

RMUs are mostly suitable for outdoor installation with minimum protection and controls. In some cases even the external control supply also not use.
 
Agree with Krisys.
Maybe you can check ABB Safeplus for more details.

Thanks,
Vijay
 
I am currently using Schneider 12kV RMU's in Minisubs (630A Isolator/200A Breaker/200A Breaker) and as a Main 11kV Switchboard 20kA we find its a cheaper option than the withdrawable
type. One can add features such as standoff trip/close facility. The VIP410E protection relay has adequate settings.
 
For the Schneider Make RMUs, you don't need a separate control power supply. It uses the self powered release mechanism. This is a specific advantage, when it comes to the remote area, where providing a dedicated control power supply is a problem.
 