Working on a historic structure, triple wythe brick walls. Brick is in fair shape, will be repaired where it isn't.
Roof at the back of the building is shot. Rafters and ceiling joists rotten at bearing. So we'll be doing repairs. 2018 Virginia Existing Building Code governs, and says the following:
Built in the 1800s, this building had zero anchorage for the roof. The rafters just sit up there. They were nailed to wood beams elsewhere, but they just sit on the brick wall with nothing but gravity and perhaps some continuity of the lapped framing to hold them down. By my reading of this code, I don't have to do anything. Naturally, that doesn't sit right with me.
So if I'm going to do something, I want to do it right...well I have about a 60plf uplift load at the wall (0.6W+0.6D). Not a lot, but when you consider we can't put unreinforced masonry into direct tension, and the interior and exterior faces of the wall cannot be touched as the historic character can't be damaged (tax credit job with State review)...things get difficult. Based on window spacings, I have to space to my anchors out about 6 or 7 feet (single course of brick over the windows). That gives me a concentrated load of about 335#. To engage a wedge of brick, I'd have to go down over 2ft. Having somebody drill a 3/4" hole over 2ft into the top of a wall 60ft above the ground to put a plate on the bottom in a small cavity that will be refilled sounds absurd from a constructability point of view. And to say "the code technically says you don't have to bother with this, but here's this challenging and potentially very dangerous detail to build, do it anyway" isn't going to go over well.
Anyone have any better ideas for concealed anchorage to historic brick?
Roof at the back of the building is shot. Rafters and ceiling joists rotten at bearing. So we'll be doing repairs. 2018 Virginia Existing Building Code governs, and says the following:
2018 VEBC 501.1 Scope said:...Repairs to historic buildings need only comply with Chapter 9.
2018 VEBC Section 903 Repairs said:903.1General.
Repairs to any portion of a historic building or structure shall be permitted with original or like materials and original methods of construction, subject to the provisions of this chapter. Hazardous materials, such as asbestos and lead-based paint, shall not be used where the code for new construction would not permit their use in buildings of similar occupancy, purpose and location.
903.2Moved buildings.
Foundations of moved historic buildings and structures shall comply with the VCC. Moved historic buildings shall otherwise be considered historic buildings for the purposes of this code. Moved historic buildings and structures shall be sited so that exterior wall and opening requirements comply with the VCC or with the compliance alternatives of this code.
903.3Replacement.
Replacement of existing or missing features using original materials shall be permitted. Partial replacement for repairs that match the original in configuration, height, and size shall be permitted. Replacement glazing in hazardous locations shall comply with the safety glazing requirements of Chapter 24 of the VCC.
Exception: Glass block walls, louvered windows, and jalousies repaired with like materials.
Built in the 1800s, this building had zero anchorage for the roof. The rafters just sit up there. They were nailed to wood beams elsewhere, but they just sit on the brick wall with nothing but gravity and perhaps some continuity of the lapped framing to hold them down. By my reading of this code, I don't have to do anything. Naturally, that doesn't sit right with me.
So if I'm going to do something, I want to do it right...well I have about a 60plf uplift load at the wall (0.6W+0.6D). Not a lot, but when you consider we can't put unreinforced masonry into direct tension, and the interior and exterior faces of the wall cannot be touched as the historic character can't be damaged (tax credit job with State review)...things get difficult. Based on window spacings, I have to space to my anchors out about 6 or 7 feet (single course of brick over the windows). That gives me a concentrated load of about 335#. To engage a wedge of brick, I'd have to go down over 2ft. Having somebody drill a 3/4" hole over 2ft into the top of a wall 60ft above the ground to put a plate on the bottom in a small cavity that will be refilled sounds absurd from a constructability point of view. And to say "the code technically says you don't have to bother with this, but here's this challenging and potentially very dangerous detail to build, do it anyway" isn't going to go over well.
Anyone have any better ideas for concealed anchorage to historic brick?