WallyFP
Specifier/Regulator
- Sep 17, 2008
- 31
Looking for guidance on how to deal with powered exhaust fans located in warehouse roofs, commonly protected by supression mode heads. Can't find anything in NFPA (other than testing is based on them not being present). FM Global used to allow sprinkler heads to be installed in the center of fans up to 4.5-ft. diameters, but that option no longer exists (in FMDS 2-0). Thoughts on shutting down with general fire alarm (water flow, pull station, etc) - similar to what is done for HVLS fans? Anybody ever take airflow measurements near AS heads to see if velocities of 5-ft./sec. exist?
Thanks for your time.
Thanks for your time.