canadeng
Mechanical
- Feb 9, 2012
- 13
Hello all, we are working on a healthcare project that involves numerous large rooftop units equipped with a common service corridor (see the enclosed picture for an example of the RTU and service corridor). These corridors are heated for service in the winter time. Units are accessed by roof only, there are no stairs the lead directly to the corridor of the unit.
I am wondering if these types of units would fall under the sprinkler exemption identified in NFPA 13 8.1.1(8), 2016 ed. "Sprinklers shall not be required to be installed within electrical equipment, mechanical
equipment, or air handling units not intended for occupancy." Given that the majority of the unit material is either non-combustible or limited combustible the fire load is likely small. However, I can see these corridors getting used for an appreciable amount of storage (i.e filter boxes).
Appreciate any comments.
I am wondering if these types of units would fall under the sprinkler exemption identified in NFPA 13 8.1.1(8), 2016 ed. "Sprinklers shall not be required to be installed within electrical equipment, mechanical
equipment, or air handling units not intended for occupancy." Given that the majority of the unit material is either non-combustible or limited combustible the fire load is likely small. However, I can see these corridors getting used for an appreciable amount of storage (i.e filter boxes).
Appreciate any comments.