I have a question regarding the temperature rise of a pump and VFD room. I used some software to calculate the heat load of the space. The software gave me this output.
Sensible gain = 28270 btuh
Latent gain = 9980 btuh
Supply Air = 1336 cfm
Coil LAT = 61 F
Now the equipment I specified can only supply 900 CFM and is capable of 36000 btuh. My question is what will be the expected room temperature?
I get around 90 F. I used q=(CFM)*1.08*(Tr-Tc), with q= 28270 btu, CFM= 900 and Tc=61 F.
Is this right? Or am I using the wrong approach?
Thanks for your help.