Rosemount 3051 Rerange 1

Status
Not open for further replies.

CMfgE1

Mechanical
Mar 15, 2005
57
Level transmitter (DP) ranged from -375"h20 (LRV) to 0"h20 (URV).
I tried to reverse this to 0"h20 (LRV) to +375"h20 (URV)
But get errors. Is there a way to successfully flip the range to make it positive?
I am using a Hart 275 for communication

Thank you
 
Replies continue below

Recommended for you

The factory does funky things with the calibration. Are you certain that you need to make this change?
My experience is with a notebook PC and AMS software using a HART modem. However, everything that you can see with the PC should be available to the handheld.

Dial the Rosemount 800 number and they should sort you out.

John
 
Well in order to do a zero cal I would think the transmitter needs to be at zero. Only when Im at 0"wc I am also at 20ma so this function doesnt work. If I try to rezero the transmitter say for height purposes I cant because it outputs 20ma and tries to make the milliamps 4 when zero shifting. I think I can perofrm these functions backwards, meaning, at 0"wc treat that as a span adj and at -375"wc as zero and do at D/A adj for the zero ma's.
Yes the factory does weird things and this is one of them.
I will keep searching.


Thanks
 
I hope you already sorted out this issue,
but anyway: try to apply a positive pressure on the negative side of the transmitter. Retry the configuration with the 275.
If it does not work try to upload Factory trim.
The transmitter will be re-set.

I am using the ABB 264 models and I am doing that using the local buttons without any external configurator..
And it works.




 
Thanks for the info. What I found was that the factory trim and ranges were set to the negative. So what I have done is learned to ignore the display. I correct the 4ma signal by trimming the zero to the LRV. This forces the output to 4ma. Then I just apply pressure and perform the cal. At the high end I just adjust the span to the URV. My standard is in positive units ("h2o) and my test is setup the same. Also we are using the 4-20ma signal to a plc input so it worked out. Thanks for the response.