silebi66
Chemical
- Dec 15, 2012
- 71
Dear professional eng-tips members:
Please bear with me if my question is too trivial for you guys. The variable frequency drive (VFD) of Blowers(2 is on/1 is spare) to be controlled the airflow distribute to the 2 aeration basins and each basin
with a dissolved oxygen (DO) monitor on top.
There are two control options.
1. DO control(fig 1)
By varying the speed of a motor (VSD or VFD), and its driven load, the airflow capacity are adjusted in direct proportion to the DO level. As the flow is proportional to the blower speed, as the DO level in the
basin is reach the set point, the blower speed will be adjusted to lower speed. But, the question bothers me is what is the set point of DO level for the air demand in aeration basin ? And , cause the controllers,
and programming necessary’s cost is high. By DO measuring in each basin and the DO controller adjusts the blower VFD motor set point at its corresponding basin DO controller is quite costly. Please advice me
that this control scheme is appropriate or not.
2. Cascade flow control (fig 2)
The control for positioning the blower inlet valve, and the final challenge is the coordination of multiple blower operation. The method for controlling the blowers is cascade control. There is no DO loop, and the
set point for the airflow controller at each basin are adjusted with flow-paced controller proportional to plant influent flow. DO meter monitored periodically with a portable meter to correlate DO levels with
influent flow. The problem is the in parallel control, whenever the next blower is required to come on line cause operating blowers are out of capacity, the following occurs :
- running blowers are adjusted to minimum airflow by closing the inlet valve.
- The next blower is started and as air demeaned increases, the inlet valves to running blowers are modulated simultaneously to increase air flow, the process is reversed as blowers are dropped off. So, one blower
may have more airflow than the other one blower. The unstable blowers running condition may occurs.
I wonder these two control option description that I wrote is correct or not.
Please kindly correct and comment on these.
Really appreciate for your kindly help.
Thank you very much.
Please bear with me if my question is too trivial for you guys. The variable frequency drive (VFD) of Blowers(2 is on/1 is spare) to be controlled the airflow distribute to the 2 aeration basins and each basin
with a dissolved oxygen (DO) monitor on top.
There are two control options.
1. DO control(fig 1)
By varying the speed of a motor (VSD or VFD), and its driven load, the airflow capacity are adjusted in direct proportion to the DO level. As the flow is proportional to the blower speed, as the DO level in the
basin is reach the set point, the blower speed will be adjusted to lower speed. But, the question bothers me is what is the set point of DO level for the air demand in aeration basin ? And , cause the controllers,
and programming necessary’s cost is high. By DO measuring in each basin and the DO controller adjusts the blower VFD motor set point at its corresponding basin DO controller is quite costly. Please advice me
that this control scheme is appropriate or not.
2. Cascade flow control (fig 2)
The control for positioning the blower inlet valve, and the final challenge is the coordination of multiple blower operation. The method for controlling the blowers is cascade control. There is no DO loop, and the
set point for the airflow controller at each basin are adjusted with flow-paced controller proportional to plant influent flow. DO meter monitored periodically with a portable meter to correlate DO levels with
influent flow. The problem is the in parallel control, whenever the next blower is required to come on line cause operating blowers are out of capacity, the following occurs :
- running blowers are adjusted to minimum airflow by closing the inlet valve.
- The next blower is started and as air demeaned increases, the inlet valves to running blowers are modulated simultaneously to increase air flow, the process is reversed as blowers are dropped off. So, one blower
may have more airflow than the other one blower. The unstable blowers running condition may occurs.
I wonder these two control option description that I wrote is correct or not.
Please kindly correct and comment on these.
Really appreciate for your kindly help.
Thank you very much.