We have been rectifying the above fault on machines in a marine application.
The machines are a SIEMENS 1FR6 454
1800 Rpm 450V 60 Hz 812 kVA @ 0.8 PF.
They are usually configured with at least 2 running insysnchronous at all times.
We suspect a contributing factor of the failure is the ships crew paralling out of synch with other machines onboard and/or with shore supply. Difficult to prove. They have automatic paralleling capability but regularly "practice" manually.
We have replaced the existing SEMIKRON semipack diode blocks with a EUPEC brand equivalent (as recommended by SIEMENS) which has a more robust housing. The SEMIKRON brand also contributed to the failure by cracking and internal contacts separting. Due to heat and rotating forces.
1. The open circuit failure of one rotating diode results in approx. 10% higher output voltage for the same excitation current. The exitation rotor is obviously a current transformer. Is this a common design as I have only witnessed a fall in voltage on other types of machines?
2. We are going to recommend installation of an In Synch relay in the Switchboard to stop out of synchronous paralleling. Where could I find more detailed information on these relays?
3. I have located some information on Rotating Diode fault detectors ( monitoring the stator excitation current ) on the internet. If the In synch relays are fitted is it usually common to have these fitted as well?
I would appreciate anyones additional comments or tips in the right direction. Especially if there is something else that I should consider.
ACCA
The machines are a SIEMENS 1FR6 454
1800 Rpm 450V 60 Hz 812 kVA @ 0.8 PF.
They are usually configured with at least 2 running insysnchronous at all times.
We suspect a contributing factor of the failure is the ships crew paralling out of synch with other machines onboard and/or with shore supply. Difficult to prove. They have automatic paralleling capability but regularly "practice" manually.
We have replaced the existing SEMIKRON semipack diode blocks with a EUPEC brand equivalent (as recommended by SIEMENS) which has a more robust housing. The SEMIKRON brand also contributed to the failure by cracking and internal contacts separting. Due to heat and rotating forces.
1. The open circuit failure of one rotating diode results in approx. 10% higher output voltage for the same excitation current. The exitation rotor is obviously a current transformer. Is this a common design as I have only witnessed a fall in voltage on other types of machines?
2. We are going to recommend installation of an In Synch relay in the Switchboard to stop out of synchronous paralleling. Where could I find more detailed information on these relays?
3. I have located some information on Rotating Diode fault detectors ( monitoring the stator excitation current ) on the internet. If the In synch relays are fitted is it usually common to have these fitted as well?
I would appreciate anyones additional comments or tips in the right direction. Especially if there is something else that I should consider.
ACCA