Rotating imbalance from faulty rotor bar joints

Status
Not open for further replies.

wetwind

Electrical
Sep 13, 2006
2
US
I have recently had some rotors tested(with a core loss tester) and the results showed some high resistance joints between the rotor bars and the short circuit ring(these are brazed joints). I know that these high resistance joints will cause vibration issues, high current draw, and heating issues. I would like to calculate(or estimate)the amount of force or imbalance that would occur from a high resistance joint in a rotor circuit. Any help would be appreciated.
 
Replies continue below

Recommended for you

The main effect would be uneven heating causing a rotor bow. The formula would be

Force = S[·]W[·]A[·]G
Where Force is in units of lbf

=====================================
Eng-tips forums: The best place on the web for engineering discussions.
 
Another effect which might occur is movement of bars within the slots. Same formula.

=====================================
Eng-tips forums: The best place on the web for engineering discussions.
 
E-pete, you had me going there for a second. I found myself trying to interpret the electrical meanings for S, W, A,... oh no!

JRaef.com
"Engineers like to solve problems. If there are no problems handily available, they will create their own problems."

Scott Adams
For the best use of Eng-Tips, please click here -> faq731-376
 
Glad you liked my formula. Maybe I should have created variables: S = Speed;
W = Weight of rotor; A = cross sectional area; G = acceleration of gravity (required for English units).

Actually I wasn't trying to be a wise guy in response to the original question. I suspect any attempt at calculating this would be very involved, require many gross assumptions, and be very inaccurate.


=====================================
Eng-tips forums: The best place on the web for engineering discussions.
 
No, no, no. Obviously, as this is an electrical forum, S = apparent power in VA, W = power in Watts, A = Current in Amperes, and G = Conductance in mhos or Siemens.

Unfortunately, the formula then also needs a term (or terms) that can cancel the extra m*A[sup]3[/sup]/s from the results.
 