Hi
1.) Euro-code seems to lack detail regarding issues such as deflection and rotation limits, now for a lintel supporting a brick wall what deflection limits are recommended. I normally used L/360 however I have heard other engineers suggest much more stringent requirements like L/500 or L/600. This does however greatly increase the beam sizes for many a project, how do other engineers deal with this?
2.) I have found little info regarding rotation limits, the SCI guide P-385 does state a maximum rotation of 3 degrees at ULS and a maximum rotation of 2 degrees at SLS, does this seem ok?
Thanks
1.) Euro-code seems to lack detail regarding issues such as deflection and rotation limits, now for a lintel supporting a brick wall what deflection limits are recommended. I normally used L/360 however I have heard other engineers suggest much more stringent requirements like L/500 or L/600. This does however greatly increase the beam sizes for many a project, how do other engineers deal with this?