Rotor ground faults without slip rings

NickParker

Electrical
Sep 1, 2017
413
What are the methods for detecting ground faults in rotor windings without using slip rings? This is for diesel generators with a capacity of 3 to 5 MVA.
Does the current injection principle for detecting ground faults require slip rings?
Is rotor earth fault detection necessary for generators in this capacity range? Can I use loss of excitation for detecting rotor earth fault detection?
 
Replies continue below

Recommended for you

Disconnect the rotating diodes and megger-test the rotor.
Also test the diodes while you have the chance.
 
No, you cannot detect rotor ground fault without sliprings. Rotor can run with single earth fault but will have damaging vibrations if it develops a second earth fault.
Loss of excitation is harder to detect and will not detect rotor earth fault.
 
GE on their 6A3 generators with brushless exciters in the 90s (and I am assuming others had this although I haven’t seen them) used a rotor mounted unit that would light an indicator when the rotor insulation was present. The light would turn off when a ground fault was detected. A stationary receiver would reset a timer when the light triggered the indicator, when the timer expired it would trigger a rotor ground fault alarm. This allowed rotor ground detection be provided without slip rings.
 