Hello fellow engineers,
I have a structural problem involving a round HSS which I hope you may help me with. This is the situation.
1. There is an HSS406x9.5 column which will receive moment from a W310x97 as well as an axial load. The factored moment is 229 kN·m and the axial load is 33 kN in compression.
2. I treated the beam flanges as transverse plates. According to my calculations the capacity of the HSS406x9.5 is 389 kN but the factored load in the compression “transverse plate” is 816 kN. Therefore, the HSS will fail under local yielding.
3. The HSS406x9.5 columns and the W310x97 beams have already been purchased and so I can’t use different sections.
4. Since the wall of the HSS406x9.5 is too thin I was asked to calculate the thickness of a doubler plate to resist local yielding. According to my calculations, the total required thickness (HSS wall+doubler plate) is 13.8 mm. Therefore, I need 4.3 mm (13.8mm-9.5mm) more. I recommend adding a 9.5 mm thick doubler plate.
My question is:
Will doubler plate and the wall of the HSS406x9.5 act together so that it’s ok to simply add a 9.5 mm thick doubler plate? I based my calculations on Table K1.1 (Transverse Plate T-and Cross-Connections) of the “Specification for Structural Steel Buildings”.
Any help would be greatly appreciated.
I have a structural problem involving a round HSS which I hope you may help me with. This is the situation.
1. There is an HSS406x9.5 column which will receive moment from a W310x97 as well as an axial load. The factored moment is 229 kN·m and the axial load is 33 kN in compression.
2. I treated the beam flanges as transverse plates. According to my calculations the capacity of the HSS406x9.5 is 389 kN but the factored load in the compression “transverse plate” is 816 kN. Therefore, the HSS will fail under local yielding.
3. The HSS406x9.5 columns and the W310x97 beams have already been purchased and so I can’t use different sections.
4. Since the wall of the HSS406x9.5 is too thin I was asked to calculate the thickness of a doubler plate to resist local yielding. According to my calculations, the total required thickness (HSS wall+doubler plate) is 13.8 mm. Therefore, I need 4.3 mm (13.8mm-9.5mm) more. I recommend adding a 9.5 mm thick doubler plate.
My question is:
Will doubler plate and the wall of the HSS406x9.5 act together so that it’s ok to simply add a 9.5 mm thick doubler plate? I based my calculations on Table K1.1 (Transverse Plate T-and Cross-Connections) of the “Specification for Structural Steel Buildings”.