I have a copy of "HVAC Equations Data and Rules of Thumb" and one of the sections has the following:
A. If heat loss exceeds 450 Btu/hr. per lineal feet of wall, heat should be provided from under the window or from the base of the wall to prevent downdrafts.
B. If heat loss is between 250 and 450 Btu/hr. per lineal feet of wall, heat should be provided from under the window or from the base of the wall, or it may be provided from overhead diffusers, located adjacent to the perimeter wall, discharg-
ing air directly downward, blanketing the exposed wall and window areas.
C. If heat loss is less than 250 Btu/hr. per lineal feet of wall, heat should be provided from under the window or from the base of the wall, or it may be provided from overhead diffusers, located adjacent to or slightly away from the perimeter wall, discharging air directed at, or both directed at and directed away from, the exposed wall and window areas.
I've also seen the 250/450 BTUH limits in other publications, namely manufacturer publications. I have tried to look for supporting evidence in more 'prestigious' publications, such as ASHRAE, ARI or even AMCA, but have had no luck.
Does anyone know where this rule of thumb originated, or if its even accurate/applicable?
A. If heat loss exceeds 450 Btu/hr. per lineal feet of wall, heat should be provided from under the window or from the base of the wall to prevent downdrafts.
B. If heat loss is between 250 and 450 Btu/hr. per lineal feet of wall, heat should be provided from under the window or from the base of the wall, or it may be provided from overhead diffusers, located adjacent to the perimeter wall, discharg-
ing air directly downward, blanketing the exposed wall and window areas.
C. If heat loss is less than 250 Btu/hr. per lineal feet of wall, heat should be provided from under the window or from the base of the wall, or it may be provided from overhead diffusers, located adjacent to or slightly away from the perimeter wall, discharging air directed at, or both directed at and directed away from, the exposed wall and window areas.
I've also seen the 250/450 BTUH limits in other publications, namely manufacturer publications. I have tried to look for supporting evidence in more 'prestigious' publications, such as ASHRAE, ARI or even AMCA, but have had no luck.
Does anyone know where this rule of thumb originated, or if its even accurate/applicable?