I am trying to run a DOL starter for a Marine Hydraulic Power Unit.
The Starter runs a 220V 3-phase 60hz 2.2kW motor.
I am in the UK and my Factory supplies are 230VAC Single Phase and 415V 3-phase.
I have tried running a VFD as the supply to the starter, but when I engage to motor contactor in the starter, the VFD triggers a constant speed overcurrent error and cuts the supply.

The starter will not allow the motor contactor to engage without 3-phase, but if the vfd is running before I start the motor, it errors and cuts the supply.

Any ideas?

(First time poster)
 
Replies continue below

Recommended for you

Or… use a VFD that is about 3x larger than the motor (using CT /HD sizing). Most drive transistors on CT/HD sized drives can handle around 200% current for 2 seconds. So given that the starting current of the motor will be roughly 6x, tripling the size of the VFD should get you there. Personally I would go next size up to be safe though.
 
Sorry for the late update, but the Starter passed the surveyor testing.

For clarity this is only the Factory Acceptance Test. It is meant as a technical demonstration that the system has the required functionality and safety features.

It will now be sent to the shipyard for installation.

Once installed, it will have to pass dry-land commissioning, afloat commissioning and finally full sea trial.
All with the vessel's own power supply and permanant cabling.
 