Do the same standards apply to the allowable pressure drops to inlet and outlet piping for a rupture disc (alone, no PSV) as for a PSV? For instance, does the pressure drop going to the rupture disc still need to be within 3% of the burst pressure? And what about the discharge piping? Does this depend on which rupture disc you buy?
 
Replies continue below

Recommended for you

No.

Good luck,
Latexman

Technically, the glass is always full - 1/2 air and 1/2 water.
 
The instant the RD blows, it's simply pipe flow, whether it is non-compressible, compressible, gas/vapor, liquid, or two phase flow. You are bound by your Code on overpressure rules though.

Good luck,
Latexman

Technically, the glass is always full - 1/2 air and 1/2 water.
 