tulum
Industrial
- Jan 13, 2004
- 335
Hey folks,
We are buying a 6.9kV - 600V 2/2.6MVA air cooled dry type transformer (7% Z min). The primary will have S&C SM5 fuses and the secondary will be a Molded case breaker (rated 35kA). The transformer is delta - Wye with a 5A NGR that is alarm only not tripped.
I have charted the SM5 fuse vs. a standard ANSI damage curve for a 2MVA transfomer and either a 250E or 300E would work. Is there any special consideration that I need to look at because the transformer is 80DegC and is actually capable of 2.6MVA continuous? Should I plot the SM5 curve against the 2.6MVA capacity curve instead or does this matter? Is the secondary Fault current calculated based on the 2MVA rating or the 2.6MVA rating?
Regards,
TULUM
We are buying a 6.9kV - 600V 2/2.6MVA air cooled dry type transformer (7% Z min). The primary will have S&C SM5 fuses and the secondary will be a Molded case breaker (rated 35kA). The transformer is delta - Wye with a 5A NGR that is alarm only not tripped.
I have charted the SM5 fuse vs. a standard ANSI damage curve for a 2MVA transfomer and either a 250E or 300E would work. Is there any special consideration that I need to look at because the transformer is 80DegC and is actually capable of 2.6MVA continuous? Should I plot the SM5 curve against the 2.6MVA capacity curve instead or does this matter? Is the secondary Fault current calculated based on the 2MVA rating or the 2.6MVA rating?
Regards,
TULUM