cc2942
Industrial
- Sep 23, 2009
- 2
I am a boiler operator. I currently operate 2 high pressure Cleaver Brooks 100 horsepower boilers. Recently, I had to shutdown one boiler due to a rupture on the feedwater supply line. The boiler I shutdown was the lagging boiler so it already had the main steam stop valve closed. Our normal operating pressure is 116 psi. The Chief Engineer schedhuled it to be repaired the next day so he ordered me to turn the boiler off but not drain the boiler cause it didnt need to be. According to Stationary Engineering books and in the vocational classes I recall that the boiler vent (also referred to as an air cock or test valve) should be opened when the pressure drops to 25 psi in order to prevent a vacuum which could cause internal damages. So i did open the vent . However, is that vacuum that is being referred to, only when draining the boiler or is their actually a vacuum formed as the pressure drops from 116 psi to 0 psi within the boiler? No books or study material seems to make that clear so I am asking an engineer? This is controversial at my job now. Please fill me in.