Hi,
I'm reviewing some safety devices for boiler and piping system according to european standards (EN 754-7..).
The set pressure of the safety valves is the design pressure of the system, and the pressure can exceed this by 10% when the safety device is operating.
The standard specifies that the pressure drop in the inlet pipe to the safety valve should be <3% of the set pressure. Also pipe sizes before/after the safety valve should not be smaller than for the safety valve.
The outlet piping should be designed so that the velocity is not supersonic and so that the 10% rule is not exceeded.
Now in the data sheet from the manufacturer the built-up back-pressure is said to be 0 bar and superimposed pressure is atmospheric.
Is it correct not to consider any built-up back pressure as long as this is below some limit (as with the 3% inlet rule) or is the safety valve specified wrong. There is of course some piping after the valve.
Is there some other rule i should know about? For example regarding maximum lengths of piping or similar.
I'm reviewing some safety devices for boiler and piping system according to european standards (EN 754-7..).
The set pressure of the safety valves is the design pressure of the system, and the pressure can exceed this by 10% when the safety device is operating.
The standard specifies that the pressure drop in the inlet pipe to the safety valve should be <3% of the set pressure. Also pipe sizes before/after the safety valve should not be smaller than for the safety valve.
The outlet piping should be designed so that the velocity is not supersonic and so that the 10% rule is not exceeded.
Now in the data sheet from the manufacturer the built-up back-pressure is said to be 0 bar and superimposed pressure is atmospheric.
Is it correct not to consider any built-up back pressure as long as this is below some limit (as with the 3% inlet rule) or is the safety valve specified wrong. There is of course some piping after the valve.
Is there some other rule i should know about? For example regarding maximum lengths of piping or similar.