Sagging Exterior PSL Deck Beam 1
XR250
I have a project where a 10-year-old exterior 3 1/2x16 PSL beam is sagging. The beam spans 18’-8” and supports 10 foot span floor joists. The beam is measured to be sagging 11/16”. I calculated it should be sagging no more than 5/16” supporting dead load only using a modulus of 1.4E6 per Weyerhauser and including a long-term creep factor of 2. I do not know who actually manufactured this beam, however. I probed the beam and it does not appear to be rotten. As such, I assume it is pressure treated,
About 15 other beams in this townhouse community are sagging similarly.
The sagging echoes what I have seen in other exterior treated engineered beams and have heard anecdotally from other contractors.
I don’t want to be the guy to condemn this beam and then have all the other townhouse owners calling me about theirs. How would y’all proceed? I’m leaning towards doing nothing.
Yes, creep and deflection can vary, but in this case, the main issue has been missed by the wood rep: the beam is sagging because it’s starting to fall apart.
Based on the picture, that looks worse than non-PT lumber that I've seen exposed to weather. I've seen timbers after fires that look better. 3/4" deflection with presumably very little actual load is not good. I would have guessed that a non-PT beam had been used in error. I can't believe the supplier both confirmed that it's PT and concluded that this is acceptable. Will definitely never spec this shit.
