dln001
Civil/Environmental
- Sep 22, 2005
- 5
I am currently working part-time for a civil engineering firm while I finish my senior year in a CE program. The engineers in my office have been wonderful teachers and recently I was given the responsibility of designing the site plan for a 120 room hotel. In the process, I exposed what I consider to be a hole in my co-workers knowledge. Sizing the sanitary line was complicated when no one could give me a definitive flow-rate for hotels. I eventually found a rate of 130 GPD per guest room (24 hours). Using a peak factor of 2 I arrived at approximately 22 GPM. Any help with sanitary sewer flow rates would be appreciated. I am located in Virginia if that has any relevance.