Dear sirs,
Per tests performed on single phase autotransformers for 53.3 MVA, 132/220 kV :factory values and site test value for 220 kV bushings is 0.353% and 0.188%.
1.Is it possible to have lower than factory values at site? These tests were done after three years on newly brought unused ones.
2. Site acceptance test shows 0.5% value. Seems okay. But difference is 0.17. in my knowledge: this should be less than 0.1 to be acceptable.
Can somebody please guide
Regards