CKent
Electrical
- Aug 27, 2003
- 42
I'd like to know why is it not usual for power transformers to be specified with short circuit rating. Our specification includes only the short circuit withstand capability which is normally the 2s duration of the short circuit symmetrical current available from the transformer which is equivalent to the base current divided by the impedance at OA rating. This is based on ANSI C57.12.00. Assymetrical value is higher depending on the K factor and could be as high as 2.824 times...
However, short circuit simulations will show that short circuit currents passing through the transformers (either towards secondary or towards another fault location) is very much bigger even than the assymetrical value which may be obtained from the above calculation based on C57.
However, short circuit simulations will show that short circuit currents passing through the transformers (either towards secondary or towards another fault location) is very much bigger even than the assymetrical value which may be obtained from the above calculation based on C57.