I am pricing out some switchgear, and I am having some problems with the ratings...
One of the non-fused switches is rated as follows:
momentary: 40ka Asym (25ka Sym)
Fault Close Current:40ka Asym (25ka Sym)
Short time Current@ 2 sec:40ka Asym (25ka Sym)
Can all these ratings be the same?? and isn't momentary equal to Short time as defined by ANSI?
I thought if;
RMS Sym = 25ka then;
momentary = 1.6*25 = 40ka = short time, and;
Peak Short time withstand = 2.6*25 = 65kA
Furthermore, how do these relate to the nomenclature I have heard people use such as Isc, Ith and Ip?
Maybe a FAQ on SC ratings - IEC and ANSI would help??!
THanks