eeprom
Electrical
- May 16, 2007
- 482
Hello,
I'm trying to get a solid understanding of NEC article 409.22 stating that an industrial control panel must be labeled with the SCCR rating. I've been reading through UL508A SB4 which (sort of) explains how to determine the SCCR rating of a panel.
In using their table for calculations, you could never make a panel with an SCCR of greater than 10kA, and 5kA is more likely. There are very few industrial applications with fault currents this low, and so this calculation becomes impractical.
So what I'd like to know is where in the code does is say I can use engineering supervision to make this calculation? I know I can get around this SCCR deal with a good fuse, but I'd like to know that I can refer to the code when an inspector says the SCCR is too high.
EE
I'm trying to get a solid understanding of NEC article 409.22 stating that an industrial control panel must be labeled with the SCCR rating. I've been reading through UL508A SB4 which (sort of) explains how to determine the SCCR rating of a panel.
In using their table for calculations, you could never make a panel with an SCCR of greater than 10kA, and 5kA is more likely. There are very few industrial applications with fault currents this low, and so this calculation becomes impractical.
So what I'd like to know is where in the code does is say I can use engineering supervision to make this calculation? I know I can get around this SCCR deal with a good fuse, but I'd like to know that I can refer to the code when an inspector says the SCCR is too high.
EE