- Jul 23, 2015
- 462
We typically design precast mezzanines for 125 PSF (or other).
Garages are designed for 40 psf. Most large pick-up trucks weigh just as much as the typical scissor man-lift. However, the man-lift area is more concentrated with lesser area.
The typical man-lift weighs approximately 4,000 LBS including allowable capacity.
When construction begins, the crew wants to put a 4,000 scissor man-lift on the mezz for various construction purposes. The mezzanine was not designed for this. However, I think that a 4,000 LB lift located anywhere on the precast plan, prior to occupancy, should not have any significant cost increase, if any at all.
We typically have to submit an inquiry to the precast supplier to get approval. We do this several times per year.
How can I provide a blanket statement on the construction documents to prevent this on-going, repeat inquiry from the General Contractor? My thought is to have this note:
"DESIGN PRECAST MEZZANINE FOR A 4,000 LB MOVABLE, SCISSOR MAN-LIFT TO BE LOCATED ANYWHERE ON PRECAST PLAN. STORAGE OR OTHER LIVE LOADS NOT ALLOWED ON SAME PLANK THAT IS TO SUPPORT MOVABLE MAN-LIFT."
Comments? Suggestions?
Thank you!
Garages are designed for 40 psf. Most large pick-up trucks weigh just as much as the typical scissor man-lift. However, the man-lift area is more concentrated with lesser area.
The typical man-lift weighs approximately 4,000 LBS including allowable capacity.
When construction begins, the crew wants to put a 4,000 scissor man-lift on the mezz for various construction purposes. The mezzanine was not designed for this. However, I think that a 4,000 LB lift located anywhere on the precast plan, prior to occupancy, should not have any significant cost increase, if any at all.
We typically have to submit an inquiry to the precast supplier to get approval. We do this several times per year.
How can I provide a blanket statement on the construction documents to prevent this on-going, repeat inquiry from the General Contractor? My thought is to have this note:
"DESIGN PRECAST MEZZANINE FOR A 4,000 LB MOVABLE, SCISSOR MAN-LIFT TO BE LOCATED ANYWHERE ON PRECAST PLAN. STORAGE OR OTHER LIVE LOADS NOT ALLOWED ON SAME PLANK THAT IS TO SUPPORT MOVABLE MAN-LIFT."
Comments? Suggestions?
Thank you!