My copy of GE's "Distribution Transformer Manual" (1991) states that the Scott connection is a three phase to TWO phase connection, and requires extra taps in the primary windings of the two xmfrs at 50% and 86.6% !
Since I am lousy at ASCII diagrams:
Transformer 1 is connected as: H1 to primary phase C, H3 to primary phase B, and an extra primary bushing (H2!) connected from the primary 50% tap to H1 of transformer 2. Transformer 2 is connected as: H1 to H2 of xmfr1, H2 is not connected, and H3 (tapped at 86.6% of primary winding) is connected to primary phase A.
The vector diagram shows two secondary phases at 90° from each other, with two possible secondary connections:
1) a 4-wire 2 phase system with separate neutral for each phase. No attempt is made to combine the neutral returns from the two phases
2) a 3-wire 2-phase system where X1 of xmfr 1 is connected to X2 of xmfr 2, and this is brought out as the neutral, with X2 of xmfr 1 and X1 of xmfr 2 as the two 'hots'.
Note that the neutral current will tend to be LARGER than either of the two phase currents if they are balanced (90° displacement vector sum)
There is a note on the page referring to this as an obsolete connection used historically to supply specially-wound two phase loads.