I am controlling a rectifier (AC to DC) for a sintering process with a SCR phase angle control.
Everything is normal at the beginning. But things go wrong when the SCR sending output command 93% or higher. Noise is coming out from the rectifier and then Eearth Fault Relay tripped the incoming power supply. We connect the power quality analyzer to the SCR output. The result as shown below. It not as what I expected. I sent this picture to the SCR supplier, but the vendor told me that the waveform is normal for a phase angle control. Anyone can tell me is it correct or normal for a SCR performance?
Below are the activities that we have done:
1. From the beginning, we suspect there is some current leakage on the rectifier. We sent the rectifier back to rectifier supplier for verification. They did the insulation and hipot test. After installed it back to the machine, same scenario happened. Power tripped when SCR output is >=93%.
2. We connect the SCR to bulb instead of rectifier. we slowly increase the SCR output from 0% to 100%. The bulbs turn on from dim to bright. But the bulb start flickering when output >=93%. Vendor told me this is due to the bulb is low load/resistance. They tested on higher load/resistance, flickering not happen. Is that correct?
Your advices will be very appreciated.
I am controlling a rectifier (AC to DC) for a sintering process with a SCR phase angle control.
Everything is normal at the beginning. But things go wrong when the SCR sending output command 93% or higher. Noise is coming out from the rectifier and then Eearth Fault Relay tripped the incoming power supply. We connect the power quality analyzer to the SCR output. The result as shown below. It not as what I expected. I sent this picture to the SCR supplier, but the vendor told me that the waveform is normal for a phase angle control. Anyone can tell me is it correct or normal for a SCR performance?
Below are the activities that we have done:
1. From the beginning, we suspect there is some current leakage on the rectifier. We sent the rectifier back to rectifier supplier for verification. They did the insulation and hipot test. After installed it back to the machine, same scenario happened. Power tripped when SCR output is >=93%.
2. We connect the SCR to bulb instead of rectifier. we slowly increase the SCR output from 0% to 100%. The bulbs turn on from dim to bright. But the bulb start flickering when output >=93%. Vendor told me this is due to the bulb is low load/resistance. They tested on higher load/resistance, flickering not happen. Is that correct?
Your advices will be very appreciated.