bspace123
Electrical
- Sep 3, 2009
- 27
Hello
I am currently trying to test a protection relay per the attached schematic. Basically, the relay has two sets of CT's connected together in parallel with the relay, which are mounted on different feeder cables. The idea is that when feeder A is reading xx Amps and feeder B is reading yy Amps, the relay will see xx - yy Amps.
The feeder B CT's are connected via 2.5mm2 4C+E cable. The feeder A CT links have been opened and this is where I have connected my test set.
When I inject per the schematic shown, my test set goes into overload. The DC resistance between A/A- B/B- and C/C- is ~13 ohms and I am only injecting 100mA. This should not overload the test set? When I short out A-/B-/C-/N- the test set works fine.
Why are these CT's overloading the test set?
Schematic link: Link
I am currently trying to test a protection relay per the attached schematic. Basically, the relay has two sets of CT's connected together in parallel with the relay, which are mounted on different feeder cables. The idea is that when feeder A is reading xx Amps and feeder B is reading yy Amps, the relay will see xx - yy Amps.
The feeder B CT's are connected via 2.5mm2 4C+E cable. The feeder A CT links have been opened and this is where I have connected my test set.
When I inject per the schematic shown, my test set goes into overload. The DC resistance between A/A- B/B- and C/C- is ~13 ohms and I am only injecting 100mA. This should not overload the test set? When I short out A-/B-/C-/N- the test set works fine.
Why are these CT's overloading the test set?
Schematic link: Link