Haroon Baloch
Electrical
- Feb 11, 2020
- 10
I'm working on a 4.16kV, 40kA-3sec, 4000A Switchboard. We need Directional Earth Fault (67N) protection on the Generators. The relay manual (Siemens 7SR2..) mentions that the polarizing quantity for the directional protection can be "calculated from the 3 phase voltage inputs or the 3Vo input". We are using a Broken Delta VT configuration to provide the 3V[sub]0[/sub] input. I want to know what should be the secondary voltage of a single phase VT (V[sub]LN[/sub]) so that when connected in Broken delta it will give 120V output during ground fault.
The Broken delta VTs from my previous work experience have connections for 120/Sqrt(3) and 120/3 V, never 120V.
One source I checked mentions that for ungrounded systems 3V[sub]0[/sub] = 3V[sub]LN[/sub] and for grounded systems 3V[sub]0[/sub] = V[sub]LN[/sub]. From this, it seems like my single phase VT secondary should be 120V not 120/3.
Am I right to go for 120V secondary in this case? Should I consider additional connection option for 120/Sqrt(3)? Please let me know and share any references, if possible.
Thanks
The Broken delta VTs from my previous work experience have connections for 120/Sqrt(3) and 120/3 V, never 120V.
One source I checked mentions that for ungrounded systems 3V[sub]0[/sub] = 3V[sub]LN[/sub] and for grounded systems 3V[sub]0[/sub] = V[sub]LN[/sub]. From this, it seems like my single phase VT secondary should be 120V not 120/3.
Am I right to go for 120V secondary in this case? Should I consider additional connection option for 120/Sqrt(3)? Please let me know and share any references, if possible.
Thanks