- Jul 11, 2013
- 2
Hi,
We recently energized a 166MVA power transformer (230kV / 34.5kV --Grounded Wye / Grounded Wye thru resistance). We recorded currents on the primary and secondary side. The primary currents were as spected (~2000Amps) but I was surprised to see current on the secondary side, these currents aren't big in magnitude ~2-3Amps. Do these currents come from the capacitance of the secondary bus? The seconday CB was open so there was only about 15mts of insulated cable.
Cheers.
We recently energized a 166MVA power transformer (230kV / 34.5kV --Grounded Wye / Grounded Wye thru resistance). We recorded currents on the primary and secondary side. The primary currents were as spected (~2000Amps) but I was surprised to see current on the secondary side, these currents aren't big in magnitude ~2-3Amps. Do these currents come from the capacitance of the secondary bus? The seconday CB was open so there was only about 15mts of insulated cable.