Zylinderkopf
Mechanical
- Dec 30, 2005
- 45
Greetings to all:
Thank you in-advance for considering my enquiry – please know that I have performed a routine “search” of this Forum and reviewed applicable API 520 and 521 Code information prior to starting this “thread”…
I have recently made a transition from refining to chemical processing and have noticed that on some of the Sect VIII Div 1 vessels, and that have agitators installed, there exists PSV installations that discharge to a Header via a metallic braided hose that has bolting flange connections at both ends.
Please, would you as a PSV-knowledgeable Engineer comment on the subject installation practice?
The API Figures seem to convey that the “spirit and intent” API Codes consider the use of only “hard-piped” discharge connections, whether to a header or to the atmosphere. However, I can not locate any language that would prohibit the use of a metallic braided hose at the PSV discharge (maybe I did not search well-enough?).
It would seem to me that an Area Equipment Inspector would have some heartburn with this because of the challenge of performing a customary wall-thickness inspection at the braided hose.
Additionally, I found an “accident investigation report” (attached) where the Operator reports a loss of containment with a subject type installation.
As such, I “think” that installing a metallic braided hose at the discharge of a PSV would not be a “best practice”, but, I can not find any Code prohibitions or any other text language that I could confirm my suspicions…
Thank you, again, in-advance for “keeping me between the ditches”.
Thank you in-advance for considering my enquiry – please know that I have performed a routine “search” of this Forum and reviewed applicable API 520 and 521 Code information prior to starting this “thread”…
I have recently made a transition from refining to chemical processing and have noticed that on some of the Sect VIII Div 1 vessels, and that have agitators installed, there exists PSV installations that discharge to a Header via a metallic braided hose that has bolting flange connections at both ends.
Please, would you as a PSV-knowledgeable Engineer comment on the subject installation practice?
The API Figures seem to convey that the “spirit and intent” API Codes consider the use of only “hard-piped” discharge connections, whether to a header or to the atmosphere. However, I can not locate any language that would prohibit the use of a metallic braided hose at the PSV discharge (maybe I did not search well-enough?).
It would seem to me that an Area Equipment Inspector would have some heartburn with this because of the challenge of performing a customary wall-thickness inspection at the braided hose.
Additionally, I found an “accident investigation report” (attached) where the Operator reports a loss of containment with a subject type installation.
As such, I “think” that installing a metallic braided hose at the discharge of a PSV would not be a “best practice”, but, I can not find any Code prohibitions or any other text language that I could confirm my suspicions…
Thank you, again, in-advance for “keeping me between the ditches”.