Seismic Analysis - Why use 2/3 Horizontal value for the Vertical Value

Status
Not open for further replies.

readethis

Mechanical
Jan 11, 2010
2
I was once told by a Structural Engineer that when evaluating for Seismic loading, the load combination for Seismic should include 2/3 Horizontal value for the Vertical Shear and 100% Horizontal Shear. However, I have not been able to justify the reasoning behind this rule of thumb. Can anyone tell me why this applies?
 
Replies continue below

Recommended for you

Load combinations are defined by the code.
Most structural engineers in the US use ASCE 7-05 for bldgs, non-structural components, and MEP anchorage.
Seismic ground shaking produces accelerations in the 3 principal directions.
Peak vertical acceleration can be estimated as 2/3 of peak horiz acceleration. However, structural engineers typically work with pseudo-accelerations (code defined "spectra"), and use SRSS.
For a typical seismic load combo, ASCE 7 requires 20% of vert pseudo-accel with 100% of max horiz seismic forces in principal direction and 30% horiz seismic forces in the perpendicular direction (in addition to dead and scaled live loads).
 