VTHokie91
Civil/Environmental
- Oct 31, 2007
- 5
I am working on my first precast big box. As big boxes go, it's not that large, at 120' by 160'. I am getting significant pushback from the wall supplier, in that the base shear quantity that I have provided is "an order of magnitude too high".
I have attempted to follow ASCE 07 in determining seismic characteristics, and determined the base shear by eqn 12.8-1 where
I believe that I have Cs under control. W is the area where we're having the intense discussion.
Section 12.7.2 defines "W" to include the dead load, with some additions for partitions, snow, equipment, etc. Section 3.1 defines "dead load" to include walls, with no exceptions. As such, I have included full dead load of all four walls.
However, this decision is being questioned, and I am told that industry standards range from a lower end of using only the upper half of each orthogonal wall, to using the full height of each orthogonal wall, to using the upper half of all four walls. I am told that using the full dead weight of all four walls exceeds typical standards of care.
But I do not see anything in ASCE 07 permitting me to use a subset of the wall weight.
I appreciate your comments.
I have attempted to follow ASCE 07 in determining seismic characteristics, and determined the base shear by eqn 12.8-1 where
V = Cs * W
I believe that I have Cs under control. W is the area where we're having the intense discussion.
Section 12.7.2 defines "W" to include the dead load, with some additions for partitions, snow, equipment, etc. Section 3.1 defines "dead load" to include walls, with no exceptions. As such, I have included full dead load of all four walls.
However, this decision is being questioned, and I am told that industry standards range from a lower end of using only the upper half of each orthogonal wall, to using the full height of each orthogonal wall, to using the upper half of all four walls. I am told that using the full dead weight of all four walls exceeds typical standards of care.
But I do not see anything in ASCE 07 permitting me to use a subset of the wall weight.
I appreciate your comments.