Hi all,
I'm curious about the AISC341-16 provisions concerning Ordinary Concentric Braced frames "OCB" (I'm in Australia so don't know the standard that well). It states that the slenderness of the braces in a "V" type configuration must satisfy
Lc/r<4sqrt(E/Fy)
I understand this seems have the intent of minimising un-favourable degradation of overly slender braces (happy to be corrected). But on appraisal in a recent project, members sized using this are so "stocky" that they would not buckle nor yield in tension under "elastic" seismic action (i.e Response Modification Coefficient R = 1.0)
This leads me to the conclusion that the connection to and overturning on the footing would also need to be sized for R=1.
Example
Consider single storey of height "h" with "V-type" OCBF
R=3.0
Seismic Shear V3=100kN
Seismic OT Moment M3 = 100h
Brace compression C3 = (0.5)1.41V3 = 70kN (45 degree angle and 0.5 to tension diagonal)
Select brace due to slenderness limit results in buckling capacity of 400kN
thus at
R=1.0
V1=300kN and Brace force is (0.5)1.41V1= 211kN<400kN
Sizing all the connections and beams for the expected capacity and/or over-strength seismic demand is one thing, but would it not make sense to size the footings for overturning from the "elastic response", otherwise the footing will do so regardless prior to any significant energy dissipation in the frame.
The potential savings in footing size may be fools gold...
Would like to hear others thoughts or experiences.
Cheers
Toby
I'm curious about the AISC341-16 provisions concerning Ordinary Concentric Braced frames "OCB" (I'm in Australia so don't know the standard that well). It states that the slenderness of the braces in a "V" type configuration must satisfy
Lc/r<4sqrt(E/Fy)
I understand this seems have the intent of minimising un-favourable degradation of overly slender braces (happy to be corrected). But on appraisal in a recent project, members sized using this are so "stocky" that they would not buckle nor yield in tension under "elastic" seismic action (i.e Response Modification Coefficient R = 1.0)
This leads me to the conclusion that the connection to and overturning on the footing would also need to be sized for R=1.
Example
Consider single storey of height "h" with "V-type" OCBF
R=3.0
Seismic Shear V3=100kN
Seismic OT Moment M3 = 100h
Brace compression C3 = (0.5)1.41V3 = 70kN (45 degree angle and 0.5 to tension diagonal)
Select brace due to slenderness limit results in buckling capacity of 400kN
thus at
R=1.0
V1=300kN and Brace force is (0.5)1.41V1= 211kN<400kN
Sizing all the connections and beams for the expected capacity and/or over-strength seismic demand is one thing, but would it not make sense to size the footings for overturning from the "elastic response", otherwise the footing will do so regardless prior to any significant energy dissipation in the frame.
The potential savings in footing size may be fools gold...
Would like to hear others thoughts or experiences.
Cheers
Toby