pwrengrds
Electrical
- Mar 11, 2002
- 233
I am involved in commissioning wind park in Calif.
They have two substations about 200 meters apart attached to a 5 mile line going to the 230kV utility grid connection. Sub 2 has been in operation for 2+ years, sub 2 is new. There are two line protection relays in sub 2, CT's in both substation are paralleled to the protection relays (SEL 311L and GE L90),and redundant SEL mirrored bit's (SEL 2506) between substation 2,3 to exchange line protection trips, breaker position, and breaker failure data.
They also use the mirrored bits to trip off substation 3 if the mirrored bits protection is lost (via loss of fiber or loss of DC to either set of the mirrored bits relay). So far substation 3 has tripped off 3 times with no indication of what the trip is in the substation, due to a missing packets going to the mirrored bits relay.
The SEL 2506 relay has DC supplied in sub 2, then the mirrored contact NC contact in sub 3 is wired to breaker trip coils of the main breaker in sub 3.
Where would I find a standard or paper on how relay failure should be dealt with. How should the relay failure be set up?
They have two substations about 200 meters apart attached to a 5 mile line going to the 230kV utility grid connection. Sub 2 has been in operation for 2+ years, sub 2 is new. There are two line protection relays in sub 2, CT's in both substation are paralleled to the protection relays (SEL 311L and GE L90),and redundant SEL mirrored bit's (SEL 2506) between substation 2,3 to exchange line protection trips, breaker position, and breaker failure data.
They also use the mirrored bits to trip off substation 3 if the mirrored bits protection is lost (via loss of fiber or loss of DC to either set of the mirrored bits relay). So far substation 3 has tripped off 3 times with no indication of what the trip is in the substation, due to a missing packets going to the mirrored bits relay.
The SEL 2506 relay has DC supplied in sub 2, then the mirrored contact NC contact in sub 3 is wired to breaker trip coils of the main breaker in sub 3.
Where would I find a standard or paper on how relay failure should be dealt with. How should the relay failure be set up?