Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Selection of cable (voltage grade) for 230/34.5kV Trafo neutral to Ground connection (Solidly ground

Status
Not open for further replies.
Feb 2, 2023
2
Dear Team,
I wanted to confirm the voltage grade for the cable to be used for connection of the 230/34.5kV transformer neutral to ground for solidly earthed system.
Should the cable be rated for 36kV?

Thanks in advance
 
Replies continue below

Recommended for you

If it is connected to ground, it doesn't have to be insulated.
 
On the contrary, I thought that since it is connected to trafo neutral, it has to be rated for L-N voltage of sec. of trafo, since during the L-G fault, the potential of the N would rise to that value, hence, cable should be rated for this voltage.
This is also being followed for the NCTs.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor