Hi gentleman,
I have done it many times but need a bit of scientific explanation to the approach I have taken.
I have a feeder entering a 2 MVA 13.8 kV transformer stepping it down to 4.16 kV Secondary which is resistance grounded with ground fault limited to 10 A NGR.
I need to have a ground fault protection on primary feeder from utility entering the transformer.I have two methods, either a residual scheme or a core balance CT.
My ground fault current from utility on primary side is 2000 A. My phase CT are 150: 5.
If I use a core balance approach, based on the fault as soon as it will pick up, relay will use TOC chr. What if it is a solid ground fault, a 2000 A ground fault will saturate a 150:5 zero seq. CT. Do you think it matters or it could be an issue.
I think It is the same issue in residual scheme, Could you guys suggest. Which one is better.
Thanks
I have done it many times but need a bit of scientific explanation to the approach I have taken.
I have a feeder entering a 2 MVA 13.8 kV transformer stepping it down to 4.16 kV Secondary which is resistance grounded with ground fault limited to 10 A NGR.
I need to have a ground fault protection on primary feeder from utility entering the transformer.I have two methods, either a residual scheme or a core balance CT.
My ground fault current from utility on primary side is 2000 A. My phase CT are 150: 5.
If I use a core balance approach, based on the fault as soon as it will pick up, relay will use TOC chr. What if it is a solid ground fault, a 2000 A ground fault will saturate a 150:5 zero seq. CT. Do you think it matters or it could be an issue.
I think It is the same issue in residual scheme, Could you guys suggest. Which one is better.