When selecting cable for high current power supplies 500A+, and a specific voltage rating of e.g. 3.3kV.
The cable is between a converter and a large motor, so the system will have some switching dv/dT over voltages, but limited by a dv/dt filter.
Do you then select a 3,3kV cable or go up a size to 6,6kV to account for any over voltages in the system that could damage the cable insulation.
I've talked to both people who insist on choosing a voltage rating one larger than the rated voltage, and people who doesn't.
When looking at cable datasheets, the cables have been tested with a spark voltage test to a voltage 2-4x times higher than the voltage rating.
Is this test a guarantee of the cables over-voltage withstand capabilities?.
Preferably do you have any information/articles mentioning this? I cannot seem to locate any.
Thanks in advance!
Best regards Jens.
When selecting cable for high current power supplies 500A+, and a specific voltage rating of e.g. 3.3kV.
The cable is between a converter and a large motor, so the system will have some switching dv/dT over voltages, but limited by a dv/dt filter.
Do you then select a 3,3kV cable or go up a size to 6,6kV to account for any over voltages in the system that could damage the cable insulation.
I've talked to both people who insist on choosing a voltage rating one larger than the rated voltage, and people who doesn't.
When looking at cable datasheets, the cables have been tested with a spark voltage test to a voltage 2-4x times higher than the voltage rating.
Is this test a guarantee of the cables over-voltage withstand capabilities?.
Preferably do you have any information/articles mentioning this? I cannot seem to locate any.
Thanks in advance!
Best regards Jens.