hello
currently , we are supervising construction of an above storage tank designed per API650
characteristics:
roof :
- dome self supported .
- D:29.03 m
- thickness =9mm .
- load from the roof = 2013404 N.
the roof was erected and welded on the ground , dimensional checking was done( it was ok) before welding but not after welding .
after the roof was erected;it was supposed to be seated on the top angle at a distance of 25 mm from the shell (refer refer to photo).
for some reason (maybe welding ) most of the roof now sits on the weld (joining the top angle and the shell) and the rest sits on the top angle properly .
my questions is:
1- contractor's proposal is to weld it as it's (which means there will be weld over a weld ), can this be done?.
2- 2nd proposal is to cut the roof's edges to make it all sit on the shell, is this feasible and are there any dimensional tolerances for the dome roof diameter and height .
thanks in advance.
3- is there any other propositions to fix it.
currently , we are supervising construction of an above storage tank designed per API650
characteristics:
roof :
- dome self supported .
- D:29.03 m
- thickness =9mm .
- load from the roof = 2013404 N.
the roof was erected and welded on the ground , dimensional checking was done( it was ok) before welding but not after welding .
after the roof was erected;it was supposed to be seated on the top angle at a distance of 25 mm from the shell (refer refer to photo).
for some reason (maybe welding ) most of the roof now sits on the weld (joining the top angle and the shell) and the rest sits on the top angle properly .
my questions is:
1- contractor's proposal is to weld it as it's (which means there will be weld over a weld ), can this be done?.
2- 2nd proposal is to cut the roof's edges to make it all sit on the shell, is this feasible and are there any dimensional tolerances for the dome roof diameter and height .
thanks in advance.
3- is there any other propositions to fix it.