Hi Everyone,
I have been arguing with a supplier of mine about a 24V DC power supply which is supposedly SELV compliant to EN 60950. When doing my usual testing of SELV supplies I measure the voltage across any two conductors on the DC side to ensure they do not exceed ELV levels (as one should expect from an SELV supply). The +ve to -ve terminals I measured as 24VDC no problem, but when I measured from either +ve or -ve to earth I got 90V AC with 50Hz ripple!
Am I going mad, or does this not comply with the requirements of SELV?
The power supply in question is a Carlo Gavazzi SPM1-241 (datasheet)
I believe this 90V AC is due to the capacitive coupling through the transformer as it is not screened and there is no earth terminal on the power supply itself. They are only relying on double insulation, but this doesn't stop the capacitance.
My supplier is arguing that this is OK as when you test to the SELV clauses in EN 60950 you only test for AC or DC depending on the supply type. They reckon that if the power supply is DC, you only need to test DC voltages. If the supply is AC you only need to test AC voltages.
I completely disagree as by this argument you can have a full exposure to 240V AC on the ELV side so long as the power supply is DC.
Does this not scream potential for electric shock to anyone else and complete void the purpose of SELV in the first place??
I have been arguing with a supplier of mine about a 24V DC power supply which is supposedly SELV compliant to EN 60950. When doing my usual testing of SELV supplies I measure the voltage across any two conductors on the DC side to ensure they do not exceed ELV levels (as one should expect from an SELV supply). The +ve to -ve terminals I measured as 24VDC no problem, but when I measured from either +ve or -ve to earth I got 90V AC with 50Hz ripple!
Am I going mad, or does this not comply with the requirements of SELV?
The power supply in question is a Carlo Gavazzi SPM1-241 (datasheet)
I believe this 90V AC is due to the capacitive coupling through the transformer as it is not screened and there is no earth terminal on the power supply itself. They are only relying on double insulation, but this doesn't stop the capacitance.
My supplier is arguing that this is OK as when you test to the SELV clauses in EN 60950 you only test for AC or DC depending on the supply type. They reckon that if the power supply is DC, you only need to test DC voltages. If the supply is AC you only need to test AC voltages.
I completely disagree as by this argument you can have a full exposure to 240V AC on the ELV side so long as the power supply is DC.
Does this not scream potential for electric shock to anyone else and complete void the purpose of SELV in the first place??