John_187
Mechanical
- Apr 21, 2018
- 68
There is a project with a server/electrical room. As such, the sensible heat ratio should be very high - very close to 1 - because there are no internal sources of humidity or people in the room.
Also, there is no real source of outdoor airflow, and this shouldn't change the sensible heat ratio, as outdoor air is a source external to the room, correct?
Due to no real presence of outdoor air and a very high sensible heat ratio, I think it is reasonable that the majority (95 %) of the cooling load on the coil will be sensible. This is determined based on the psychometric chart and the logic that the coil will dry out the constantly recirculating room air to a humidity ratio equal to that of the cooling supply air at 55 F.
The reason I'm asking, is that often manufacturer's publish data about cooling coils - saying for example - 50,000 Btu/hr sensible, 70,000 Btu/hr total. However, that doesn't mean that the coil isn't CAPABLE of having the vast majority (95 %) of the total load be sensible right? There is no limiting factor on what percent of a coil load is sensible or latent, it is strictly determined by the conditions that the coil is subjected to?
Please comment on the above assumptions/questions, thanks for your time
Also, there is no real source of outdoor airflow, and this shouldn't change the sensible heat ratio, as outdoor air is a source external to the room, correct?
Due to no real presence of outdoor air and a very high sensible heat ratio, I think it is reasonable that the majority (95 %) of the cooling load on the coil will be sensible. This is determined based on the psychometric chart and the logic that the coil will dry out the constantly recirculating room air to a humidity ratio equal to that of the cooling supply air at 55 F.
The reason I'm asking, is that often manufacturer's publish data about cooling coils - saying for example - 50,000 Btu/hr sensible, 70,000 Btu/hr total. However, that doesn't mean that the coil isn't CAPABLE of having the vast majority (95 %) of the total load be sensible right? There is no limiting factor on what percent of a coil load is sensible or latent, it is strictly determined by the conditions that the coil is subjected to?
Please comment on the above assumptions/questions, thanks for your time