PagoMitch
Mechanical
- Sep 18, 2003
- 66
Doing some Hospital HVAC in the Tropics, on an island where much of the population are persons of size.
ASHRAE lists values from 245S/105L for sitting, to 250S/250L for standing and walking.
However, I cannot find any references - anywhere - of how these values are affected by persons of size, turn-over of same (people entering/leaving), and external ambient conditions.
In this case, external conditions are 91DB/82WB. Wherever you go outside, hot and sweaty is the norm. And whenever you go indoors, you drag a lot of that heat and moisture with you.
I used to live there and worked at the hospital as the Facility Engineer. During that time, I had always used 300 BTUH Sensible and 300 BTUH Latent for individuals for HVAC design. This was based on my observations that whenever a 250-300 lb person comes in (realistically, 75% of the adult population) and sits down, you can feel the heat radiating off them from literally a foot away, for 15-20 minutes.
If this were a library, where people come in and sit for hours on end, this would not be as critical.
But for a Hospital Waiting Rm, which continually has people entering and leaving, the extra heat/water vapor per person adds up.
So.
Has anybody seen an official reference to increase the individual person BTUH S/L beyond the "usual" ASHRAE values?
I am convinced of the validity of this approach, because I have experienced it; but I am looking for something to substantiate and quantify (higher? lower?) my experience.
TIA.
ASHRAE lists values from 245S/105L for sitting, to 250S/250L for standing and walking.
However, I cannot find any references - anywhere - of how these values are affected by persons of size, turn-over of same (people entering/leaving), and external ambient conditions.
In this case, external conditions are 91DB/82WB. Wherever you go outside, hot and sweaty is the norm. And whenever you go indoors, you drag a lot of that heat and moisture with you.
I used to live there and worked at the hospital as the Facility Engineer. During that time, I had always used 300 BTUH Sensible and 300 BTUH Latent for individuals for HVAC design. This was based on my observations that whenever a 250-300 lb person comes in (realistically, 75% of the adult population) and sits down, you can feel the heat radiating off them from literally a foot away, for 15-20 minutes.
If this were a library, where people come in and sit for hours on end, this would not be as critical.
But for a Hospital Waiting Rm, which continually has people entering and leaving, the extra heat/water vapor per person adds up.
So.
Has anybody seen an official reference to increase the individual person BTUH S/L beyond the "usual" ASHRAE values?
I am convinced of the validity of this approach, because I have experienced it; but I am looking for something to substantiate and quantify (higher? lower?) my experience.
TIA.