nightrider
Mechanical
- Nov 20, 2000
- 5
A. I am trying to get the heat load of all the existing connected equipment and other heat generating apparatus as well as the proposed ones in a laboratory to determine the right a/c size, I calculate the sensible heat load by using the nameplate data in watts multiplied by 3.4 how about the latent heat load, it's ok if there is an equipment of the same rating or falls within the range from table of recommended rate of heat gain. Ashrae
B. Also can I conclude that for the fumehood there will be no heat gain for heat gain is equal to heat loss due to its outdoor supply and exhaust unit that is electrically interlocked mounted on the roof.
I would greatly appreciate if anyone out there could provide me a solution. Thank you.
B. Also can I conclude that for the fumehood there will be no heat gain for heat gain is equal to heat loss due to its outdoor supply and exhaust unit that is electrically interlocked mounted on the roof.
I would greatly appreciate if anyone out there could provide me a solution. Thank you.