Hi All,
I am trying to establish seperation distance requirements between a Generator (outdoor) and a Building.
The 2MVA generator has a 3000L diesel fuel day tank (790 US Gal). The tank is integral to the generator package and located beneath the engine.
The building exterior wall does not have any fire resistance.
NFPA 37 (4.1.4) specifies a separation distance of 1.5m (5ft).
I have also checked NFPA 110 (5.6.1), which refers back to NFPA 37.
I have also looked at NFPA 30, with respect to the size of the fuel tank. Table 15.3 provides separation distances for outdoor storage. However, I believe that the integral fuel tank on the generator cannot be classified as a 'drum', a 'protable tank' or an 'intermediate bulk container'.
In which case my conclusion is that 1.5m is the required seperation distance.
Any comments?
Thanks.
I am trying to establish seperation distance requirements between a Generator (outdoor) and a Building.
The 2MVA generator has a 3000L diesel fuel day tank (790 US Gal). The tank is integral to the generator package and located beneath the engine.
The building exterior wall does not have any fire resistance.
NFPA 37 (4.1.4) specifies a separation distance of 1.5m (5ft).
I have also checked NFPA 110 (5.6.1), which refers back to NFPA 37.
I have also looked at NFPA 30, with respect to the size of the fuel tank. Table 15.3 provides separation distances for outdoor storage. However, I believe that the integral fuel tank on the generator cannot be classified as a 'drum', a 'protable tank' or an 'intermediate bulk container'.
In which case my conclusion is that 1.5m is the required seperation distance.
Any comments?
Thanks.