RHTPE
Structural
- Jun 11, 2008
- 702
I have been asked to submit a proposal for certifying precast concrete septic tanks for compliance with ASTM C1227-09. The client is using non-metallic fibers to replace welded wire fabric in the walls of the tank. Some #3 bars are used in the top slab each side of the required openings, but that is the only rebar in the tank. I have advised my client that the most definitive method of ensuring certification is to vacuum test the tank - first to the 5" of Hg for leakage (CT requirements, not ASTM), then to an amount that would be equivalent to 1.5 times the design loading. This could likely be as much 18" of Hg.
I am seeking comments from those more knowledgeable/experienced than I on these 2 topics:
1) The actual design loading on the tanks varies - perhaps 660 psf on the top, varying to as much as 1125 psf against the walls at the bottom, with hydrostatic upift on the bottom varying with ground water level. Testing by vacuum will exert a uniform load over all surfaces of the tank, unlike what it would experience in the ground. Would you expect to apply a vacuum to reach the highest magnitude of expected design loading?
2) Does anyone know of a good resource for an analytical approach to the structural design of fiber-reinforced concrete? While it may not comply with ASTM C1227-09 (requires design per ACI 318), it could provide a good starting point, particularly for fiber dosage.
Ralph
Structures Consulting
Northeast USA